Shutoff valves on automatic feeds
Greg_38
Member Posts: 3
Should the shutoff valve be left open to the automatic feed on a hot water boiler after filling. If you have a run away burner (ie stuck gas valve) the boiler starts steaming, blows the T&P valve, pressure stays up, no water added, but when it is empty (and very hot), the pressure goes down, the automatic feed opens, and you have cold water going into a very hot boiler. Makes for a "boiler room disturbance".
0
Comments
-
LWCO
With a LWCO or flow switch there is no debate - leave it closed.0 -
Tough Call
My old boss used to ALWAYS shut the feed valve off after the system was purged; however, we are required to use LWCO's here in Maine.
In my experience, I must say that I have experienced more problems with a system overfeeding rather than underfeeding, and that shutting off the feed has been beneficial. Unfortunately, one has to follow the rules of The Authority Having Jurisdiction (AHJ) in order to be legal and non-liable. Ask your Insurance company.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Antifreeze?
When anti freeze is in the system, we shut off the water feed to keep from diluting it in the event of a leak. If the customer is home all year round, we leave it on. Either way we tell customers to turn off the domestic water if they leave the structure unattended for any length of time.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements