setting vaporstat cut in/cut out
Garret
Member Posts: 111
I'm about ready to fire up the new boiler for the coming heating season...
This is two pipe steam, small vapor system... new Peerless 61 boiler. More details and pics here...
http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=261364
I'm working through the lost art, looking at Dan's instructions on calculating the pressure drop in the system.... Can someone check my math to see if I'm doing this correctly?
The supply piping for my furthest radiator is 60ft. So at 1 oz/100ft, and doubling the longest run to allow for fittings, etc.... I get 1.2 oz of pressure drop.
Doubling that, I get a cut in pressure of 2.4 oz.
Seems very low, but maybe worth a shot... I can always raise it a touch if the furthest rad doesn't heat.
Now, how do I get the cut out pressure?
Thanks!
-Garret
This is two pipe steam, small vapor system... new Peerless 61 boiler. More details and pics here...
http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=261364
I'm working through the lost art, looking at Dan's instructions on calculating the pressure drop in the system.... Can someone check my math to see if I'm doing this correctly?
The supply piping for my furthest radiator is 60ft. So at 1 oz/100ft, and doubling the longest run to allow for fittings, etc.... I get 1.2 oz of pressure drop.
Doubling that, I get a cut in pressure of 2.4 oz.
Seems very low, but maybe worth a shot... I can always raise it a touch if the furthest rad doesn't heat.
Now, how do I get the cut out pressure?
Thanks!
-Garret
0
Comments
-
bump
0 -
set your vaporstat
for about 3 ounces cut out and 2 differential..see if all heats well..we generally use a trial & error method based upon experiance..
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements