taco circ relay
bob_17
Member Posts: 14
I have a 4 zone relay on a 3 zone system. I would like to use the 4th zone to opperate the primary loop circ. If I were to wire the end switch to t-t on the 4th zone the primary circ. would never shut down when nothing calling for heat. It seems I should be able to cut a tab off the relay cube so it wouldn't actiideas??vate the end switch. Any ideas?
0
Comments
-
Why not just
use the ZR output as the hot lead to the primary circ? On that control, when there is a zone demand, the ZR becomes hot. That is if it's a Taco SR series. I don't know about other SR's
Jed0 -
Or
Run a hot lead to one side of the isolated end switch and power the primary circ with the other side of the end switch . Taco has a great diagram book for all sorts of wiring scenerios -
http://www.taco-hvac.com/uploads/FileLibrary/100-9.0.pdf0 -
Ron,
Doesn't it depend on the XX is firing the burner? Is XX running to tt on the aquastat, or can it handle the LV?
Jed0 -
Maybe
we should ask what kind of aquastat is being used and how it's currently wired .
For a triple aquastat we connect ZC to ZC and ZR to ZR from aquastat to relay . Which frees up the dry contact end switch for primary circ control .0 -
Thanks for the feedback. It,s a gas fired boiler with electronic ignition. XX is being used to fire the boiler. If I could get the zone that powers the primary pump to NOT activate xx than I believe it would be ok. There must be a tab on the CUBE that activates xx.0 -
testing
testing0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements