Using chemical additives to clean the boiler, questions.
ttekushan_3
ttekushan_3 Member Posts: 965
Looking at the corrosion in the above photo, where is the oxygen coming from? Or do you suppose this is from caustic attack.
Saying no to chemicals without any knowledge of regional water supply chemistry or knowing whether the pH is properly controlled makes for a fairly dogmatic decision. If your region has fairly soft water (low turbidity) I wouldn't use a regular water treatment for low pressure steam with cast iron. Funny. All of the steam boiler failures I've seen around my region are boiler scale and oxygen corrosion related. Not to mention efficiency losses involved. Not a water treatment in sight on those.
-terry
Terry T
steam; proportioned minitube; trapless; jet pump return; vac vent. New Yorker CGS30C
  • Adam_24
    Adam_24 Member Posts: 36
    Chemicals or no chemicals
    Hi,
    We are being told that it is manufacturer's recommendations to add chemical cleaner to the boiler after install to clean out an oil residue on the inside. Is this always done? Is it a standard practice or is there controversy about it? We feel slightly uneasy with this recommendation. Also with further recommendation to continue to add chemicals annually to keep the system clean.
    To our knowledge no service person has ever put chemicals into our system to clean it. I know we asked once too and can't remember what the reason was, but we were told not to add them.
    I have concerns also that whatever chemical was added could leave a residue behind in the pipes and we could get some of that up into the house through the radiators. Also, wondering if you are just loosening up the stuff inside the pipes and causing more of it to end up in the boiler?
    What is the problem with NOT using the chemicals? Any?
    Thanks for your help :-)
  • gerry gill
    gerry gill Member Posts: 3,084
    how would you
    keep the ph level up if something isn't added..rhomar makes good boiler chemicals..they've a link under virtual trade show at the top..
    gwgillplumbingandheating.com
  • hr
    hr Member Posts: 6,106
    It has become more of an issue
    with the modern mod con boilers. Very small heat exchangers and multi metal construction make clean HX surfaces more of an issue.
    Many of the new mod con boilers have aluminum HX Weil, Burnham, Crown, Buderus, SlantFin and others. Water quality and cleaning will be a big issue for this type of boiler.
    Probably one that will sneak up on you after several years in service.
    Proper glycol is another one to watch, especially with aluminum and it's ph sensitivity.
    Clean em, treat'em and check them yearly. Both an inside clean and check and a ph test on the fluid should be mandatory.
    hot rod
  • Bill Jirik,
    Bill Jirik, Member Posts: 54
    chemicals
    Cleaning out the system on a new install is definately a good idea something is simple as Trisodium Phosphate, available at most hardware or paint stores, is an old standby for removing oil, flux and manufacturing residue.
    As far as ongoing treatment a lot of factors must be considered, type of system-steam or hotwater, amount of makeup water, water quality, system size, piping and boiler type-copper, steel or cast iron, a lot of factors to consider when choosing an ongoing water treatment. One thought to consider is why did you replace the old boiler and was there something you could have done to prevent what I assume was it's failure?
  • Adam_24
    steam system not hot water...
    Hi, I should have made clear this is a steam system not hot water. Does that make a difference and were the above responses for a steam system?
  • Ken_40
    Ken_40 Member Posts: 1,310
    Like my wife says:
    "You can never be too thin, too rich or have boiler water that is too clean"!
    Steam, hot water or radiant; ALWAYS USE A DETERGENT TO CLEAN OUT: Old rust and "muck," flux residue (extremely active corrosive), boiler manufacturing oils used to drill and tap waterway components and piping, pipe dope you may use that should never be allowed to run-a-round the system, and any other chemical soup compounds that will remain...
    We use TSP. It's cheap, readily available and safe to handle. If not completely rinsed out, it leaves a pH resildual that is above neutral (7.0), and becomes a rust inhibitor of sorts - which is a good thing.
  • Steve L.
    Steve L. Member Posts: 35
    I use TSP. No problems.
  • subcooler
    subcooler Member Posts: 140
    treatment
    It's one thing to flush and clean a new boiler, but if you have a nice tight clean system and your running low pressure steam or low pressure hot water treatment is crazy. After saying that I do like the customers that do run treatment. I get more boiler repair work from treated boilers than not treated. Guess which unit got the treatment from a big name chemical company? These units are both cared for by the same person.
  • Harold
    Harold Member Posts: 249
    Just curious. If leftover manufacturing residue in the core is a problem it would seem that manufacturers should clean it before shipping. If they test each boiler off the line it should be simple to flush at this stage. Do any manufacturers do this? What is their view of initial cleaning?
  • Ken_40
    Harold,
    We seem to be faced with two potential problems: One, to clean the oils which are admittedly problematic; or have them ship the boiler "clean" and have surface rust attack the female threads, forcing us to chase them upon receiving the boiler.
    I agree with the manufacturers. Since I'll have to clean the boiler anyhow of flux, pipe dope and god-knows what else, I'd rather not have to clean the threads of rust; rather the cutting oil - any day...
  • Harold
    Interesting. I was kind of thinking along the lines of pex and crimped copper. I was not thinking about lots of soldered copper. I know better but was not thinking sufficiently of all cases. My question was stimulated by my system. It is all pex and crimped copper and it was not cleaned when put into service because the assembly should not have generated junk. I don't know if there are any oil residues on the copper although I have never noticed anything when working with it. Perhaps in such systems it would be easier to just flush the boiler before installation. It is probably to late to do anything with mine because it is full of many gallons of glycol which I sure don't want to throw away.
  • Ken_40
    Glycol
    Glycol alone - can be a problem!
    Even well inhibited glycol becomes highly acidic ove a relatively short period, depending on the base metals and oxides that occur - or existed before the system was even altered.
    I would NEVER put glycol in a system that was not totally chemically cleaned - and well rinsed. Trace compounds and glycol and its inhibitors creat chemical soups that can be highly corrosive, destabilizing to all aspects of the system and the pipe dope, unless teflon tape, will leach into the soup creating compounds that will simply vary in nature - none of which is beneficial.
    I urge you to fire the boiler, let it get to at least 140 and take a system sample. With an iron and pH tester, see what you have. I'd also test the glycol concentration and determine the real frost protection point present.
    The revelation could save you a fortune in the longevity issues associated with just water quaility.
  • Drew_2
    Drew_2 Member Posts: 158
    Glycol
    Ken, you wrote;
    "Even well inhibited glycol becomes highly acidic over a relatively short period"
    How long a period?
  • Ken_40
    We have found...
    The speed with which the inhibitors lose their effectiveness is directly proportional to the cleanliness of the system - prior to introducing the glycol.
    The system operating temperature also has a profound effect.
    Using the SWAG method, I would offer the following:
    In well cleaned systems (prior to adding glycol) and with maximum water temps of ~160F, raw glycol would be harmless for two heating seasons.
    In well cleaned systems, and with a mximum water temp of 190F (180 avg. design-day) water temps; make that one heating season.
    In a "non" well cleaned system, raw glycol would cause damage before one season of use.
    In a "non" well cleaned system, inhibited glycol would last two seasons before becoming corrosive and damaging stuff.
    In a well cleaned system, and water temps never going above 160F, inhibited glycol would probably last five years.
    Remember, these are SWAG estimates!
    Although everyone says automotive glycol, Prestone or Dow is "bad" for heating systems, I still have lingering doubts as to the scientific basis of that claim.
    Consider this: Car engines frequently run at 230F. And, at 15 p.s.i. Aluminum heads are the norm. Blocks are cast iron. Copper in the radiator was prevelant, rubber, neoprene, plastics and viton as well as nylon are used extensively in antifreeze contact components.
    Car engines do ~12,000 miles a year. We change anti-freeze ~ every 3 to 5 years. Assuming 30 MPH as the average (idling at lights, city driving and 70 on highways) - that's 400 hrs. a year - for 3-5 years.
    When's the last time an engine was blown from rust or corrosion?
    Stuff to think about; n'cest pa?
  • subcooler
    Words
    I don’t want to confuse the idea of providing good water to the boiler and stating that every boiler needs chemicals added or it won’t run right. Do we want a low TDS count
    and the PH in range? Yes. Do I want to use a ton of corrosive chemicals to get it there no.
  • realolman
    realolman Member Posts: 513
    Yer wife
    don't really say that does she?
    hot_rod Member Posts: 27,472
    It's the blend water also
    that will use up the inhibitor package from the get go. Really the glycol itself doesn't go bad, it's basically a petro product. it's the inhibitors that go bad and cause the ph swing. From what I have learned.
    Consider what solder flux is comprised of... Zinc Chloride for the most part. Not a good mix for inhibited glycols.
    Or stainless boilers and indirects for that matter :)
    Overheating and frying glycol is another quick death. solar panels that stagnet and get in excess of 350 will ruin glycol inhibitors in a short period of time.
    Glycols that go acidic can be salvaged with additional inhibitors. It just takes a boat load if the ph drops into the 7's or lower. At some point it becomes less expensive to dump, clean and start over.
    hot rod
  • Darrell
    Darrell Member Posts: 303
    You guys need to tone it down a bit...I make a lot of money fixing trashed systems where the glycol wil take the hair off your knuckles its so acidic! Zonevalves, especially honeywell, air vents, relief valves, fill valves, and expansion tanks...geez...I better go check my van for stock!
  • Drew_2
    Inhibitors and antifreeze
    Cleaning a system is important. New systems to flush out residue or older systems that have scale buildup. (See attached chart) That said, here is some information about antifreeze
    Most antifreezes (propylene, ethylene ,synthetics) break down because of amount of heat and oxygen. Because we need to heat the fluid there is little we can do, other than not run the system at a higher temp than needed. In closed systems most of the oxygen is released from the fluid. Adding new water or leaks in the system will introduce new oxygen. Acid is the end result of the antifreeze breakdown. The inhibitor in standard system antifreeze has a high pH. This works as an anti-corrosion agent and a buffer to the acid created. So, from a heat stand point the hotter you make the fluid and the longer you heat it, the quicker it will breakdown.
    I received sample of propylene glycol antifreeze, daily, for testing. I have seen samples that were 3 weeks old that was brown and smelled like burned transmission fluid. Found they had a burner problem on a new system and burned the fluid. On the other end of the spectrum, I've tested a samople from a home owner that took care of his own system by checking the fluid for pH and glycol content and adding inhibitor when needed. The result was a very good fluid that had been in the system for 17 years.
    The reason that you would not want to use Automotive antifreeze in a boiler is that auto antifeezes use silicates. The reason for this is that it is an inexpensive inhibitor. Silicates coat the inside of the system with a coating that we used to refer to as Snot. This inhibitor works in vehicles because they are run on a regular basis 365 days a year. If left in a system for an extented period of time ( The off heating season) the silicate will drop out of the fluid and settle to the low point. Once this happens, even if heated, it will not disolve back into the fluid, cloging the system. If anyone would like formulas and data on automotive antifreezes, give me a call. 800-678-6625.
    Inhibitors for aluminum/multimetal systems is another 5 pages for the highlights. Maybe next time.
  • ttekushan_3
    a HA! Maybe its worth using a hydronic heating system antifreeze in a collector car's cooling system that is used infrequently and is stored in the winter?
    Any downside to that other than the cost?
    Thanks for this explanation of antifreeze components, Drew.
    -Terry
    Terry T
  • Big Ed
    Big Ed Member Posts: 1,117
    Found No Need.
    I found it is not needed to add chemicals to clean a steam boiler.Why take a chance ?
    Blow down and skim is all that's needed in my part of the world.
    If it ante broke , don't break it...
    I think adding chemicals are a easy sell so the installer does not have to return at a later date to clean boiler... Sorry not happening ....
  • Big Ed
    flux ?
    What is flux doing in a steam system ?