Calling Dan H.
FRANK_24
Member Posts: 80
We went to see Sr. Joanne at St. Stan's today. After spending a few hours sizing the school and convent, and wondering what was done by whom and why, the good Sister told us she was related to you, Dan.
The existing cast iron boiler has a fist sized hole way up high. [another dead soldier]...too much fresh water added, do ya think? There is another boiler that doesn't work that's connected to the header. Figuring out the installed loads... one is too small and two are too big. No lead lag either.
Both the school and the convent have the same problem....the second floor gets way overheated while the third floor is cold. First floor...no complaints.
What a shame the things done to that system. A two pipe steam system, without rad traps in the school,but air valves and a big ole 2" master steam trap on the single convent return, then another one after the return manifold [one convent, one wet, three dry] and before the way too small condensate reciever/pump whose piping looks like a "Lazy-bar-Z".
Naturally there is no money to replace traps in the convent, or do the right thing. "Just replace the boiler."
If I can't do the right thing, I don't want the job....then what happens to me in the after-life??? not helping the good sisters an' all. God help me. bwdik?ijap
The existing cast iron boiler has a fist sized hole way up high. [another dead soldier]...too much fresh water added, do ya think? There is another boiler that doesn't work that's connected to the header. Figuring out the installed loads... one is too small and two are too big. No lead lag either.
Both the school and the convent have the same problem....the second floor gets way overheated while the third floor is cold. First floor...no complaints.
What a shame the things done to that system. A two pipe steam system, without rad traps in the school,but air valves and a big ole 2" master steam trap on the single convent return, then another one after the return manifold [one convent, one wet, three dry] and before the way too small condensate reciever/pump whose piping looks like a "Lazy-bar-Z".
Naturally there is no money to replace traps in the convent, or do the right thing. "Just replace the boiler."
If I can't do the right thing, I don't want the job....then what happens to me in the after-life??? not helping the good sisters an' all. God help me. bwdik?ijap
0
Comments
-
You are in a difficult situation, Think that if you don't help the good sisters, Who is going to put the good words(prayers) for you with the Big Boss (GOD). If you don't help the sisters maybe you ended up in a room full of steam, lots of steam down under.I'll be praying for you and God Bless your Soul. :-)0 -
What did Dan say
about Relatives and churches?0 -
She's Marianne's cousin
and if you can't do it right, don't do it. I agree 100%.Retired and loving it.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements