main steam vent

gerry gill
gerry gill Member Posts: 3,078
then see how things work..no steam should come out of it 'less you have a bad trap..don't leave it this way..just do it for a test, then report back..

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=360&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

Comments

  • ryan
    ryan Member Posts: 23
    two pipe steam main vent

    I have a two pipe system with one main vent on the return. Some of the distant radiators do not heat well. Shouldn't I hear the vent working?
  • ryan_7
    ryan_7 Member Posts: 50


    Ok, I took it out, and nothing, no air or steam.
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    That sounds bad

    you may have a leak in your boiler, above the waterline. This would let a lot of steam go up the chimney.

    With the boiler off and cold, open the fill valve until water completely fills the boiler and rises into the outlet pipes. If you now get water on the floor, you have found the problem, and will need to replace the boiler.

    If the boiler is not leaking, be sure to drain it out to the normal water level before restarting it.