expansion tank - 2 instead of 1?
Jeff Lewis
Member Posts: 16
I am working on an install of a Munchkin boiler to power domestic hot water (80 gal) and radiant floor heat. The boiler supplier says that I need an expansion tank size 60. The radiant floor zones are already done, with an expansion tank size 30 in that loop. Can I just add another size 30 in my primary loop and be OK, or should I go with a 60 on the primary? Can you have too much expansion capacity?
0
Comments
-
I use multiple ET's often.
Partially for redundancy and also that two 30's are often less money than a single larger tank. So long as the acceptance volume is equivalent and the pressures in the tanks are equal they will perform as well as a single tank.
I usually manifold them with lock shield valves to prevent tampering and allow change-out should a bladder rupture. But I take a single connection pipe from the common manifold at the ET's to the PONPC connection upstream of the circulator. As I know you will
Not sure what your water volume is, sounds like a lot for what should be small-ish pipe and a lot more tubing. (Not like it is an old gravity system or anything.) Just a thought but no harm in too much tank within reason.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements