i am installing a w/m ultra boiler which serves an indirect fired water heater, a high temperature baseboard zone and various radiant running at 115 degrees. any suggestions on the best way to get my mixing done. I am utilizing primary secondary.
thanks jh
thanks jh
0
Comments
-
How much do you want to spend?
> i am installing a w/m ultra boiler which serves
> an indirect fired water heater, a high
> temperature baseboard zone and various radiant
> running at 115 degrees. any suggestions on the
> best way to get my mixing done. I am utilizing
> primary secondary.
>
> thanks jh
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
How much do you want to spend?
> i am installing a w/m ultra boiler which serves
> an indirect fired water heater, a high
> temperature baseboard zone and various radiant
> running at 115 degrees. any suggestions on the
> best way to get my mixing done. I am utilizing
> primary secondary.
>
> thanks jh
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
How much do you want to spend?
A simple method would be to use the outdoor reset feature for the high temperature and install a manual 3 way mix valve that tracks along with the reset curve, for the radiant temperatures.
That boiler has a DHW priority, built into the board, to handle DHW. Pipe it (the DHW circ) as a seperate loop off the additional tappings. Be sure to use flow checks, or check flanges on both circs. I think the installation manual shows some piping options for what you are trying to do.
The on board control may run two temperatures? I have not gotten into tha control that deep?
Design your high temperature loop to meet the load with the lowest possible temperature. It may be possible to beef up the baseboard lengths or higher output board to run lower temperatures at design day. The lower the operating temperature the more efficient a condensing boiler operates. Any way to design the high temperature loop emitters at around a 140°F supply ?
That's an expensive boiler to run a 180° system, if that is what is really needed.
hot rod0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 932 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements