running hot water through cast iron radiators
Bryan_17
Member Posts: 4
New construction job: 1. What is the best way to pipe in a hot water system using recessed cast iron sun rads?
2. How do I figure heat loss calculation?
2. How do I figure heat loss calculation?
0
Comments
-
First
click on the "free heat loss calcs" link at the upper left. This will get you Slant/Fin's calc program which is very easy to use.
Once you know what your heat losses are you can determine your water temp and size your Sunrads.
Piping the Sunrads can be done several ways. You can use a Monoflo system (one main with diverter tees) or a two-pipe system. Two-pipe can be done using a flow and return main, or each rad can be a "home run" to a manifold in the boiler room.
The best method depends on the building's layout and the degree of control you want.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 932 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements