varivalve

Keith_8
Keith_8 Member Posts: 399
Anybody have feedback on the Varivalve by Heat Timer?

Seems to be a efficient way to vent a One Pipe system.

Keith

Comments

  • Ken_8
    Ken_8 Member Posts: 1,640
    We find them to be

    very good. The fixed orifice Gorton's though are as good a choice as well. Larger chamber for water vapor to slow down enough to never get ejected and the fixed rather than variable setting prevents owner "twiddling" which can negate a decent vent system from working at all!

    The tendency seems to be to set each vari-vent too far open - resulting in oversized or close to the boiler rads to overheat (or make it appear the others underheat) and create as many problems as they cure...

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • keith
    keith Member Posts: 224
    Vent

    Thanks Ken,
    Keith