Glycol effect on boiler and heat exchanger rating

Dave_12
Dave_12 Member Posts: 77
Does anybody have some design information regarding derating boiler output and heat exchanger output when using glycol in hydronic heating systems.

Comments

  • Drew_2
    Drew_2 Member Posts: 158
    Glycol

    How much glycol or what temp. do you want to protect to?
  • flange
    flange Member Posts: 153


    Ethylene or propylene? should be prop. typical concentrations range around 40% for protection unless you are in a really cold climate. to calculate you need to know concentration, then charge specific gravity versus water. your pump horsepower will go up due to more dense fluid, as well as heat transfer going down. typical results at roughly fifteen percent more or less.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,517


    if you go to the raypak boiler web site and go to tech information, yhey have all kinds of information on glycol and its effect on heating systems.

    ed
  • Dave_12
    Dave_12 Member Posts: 77
    Thanks for the help

    Ebebratt:

    Thanks for the help. The Raypak website, tech help, was useful. Thanks again.

    Dave