outdoor reset
Mike T., Swampeast MO
Member Posts: 6,928
Can you describe your system? What sort of heat emitters? Approximate age? Has it been substantially changed over its lifetime?
What fuel? What boiler?
outdoor reset
Have a Burnham gas fired HW boiler newly installed. Any suggestions re:outdoor reset. My plumber says that Taco makes one that's alot less expensive than the Teckmar. What's the difference. Also, I read about systems that continue the circulator pumps after the boiler shuts down so as to take advantage of residual heat. Is this cost effective and advisable?
Dave0 -
Gas fired new Burnham boiler with a mixture of cast iron radiators and baseboard.0 -
That's a difficult mix when it comes to reset because they will have significantly different reset curve requirements. It's also quite likely that the iron radiators need a MUCH lower temperature if supplied constantly with heat.
A simple mechanical reset controller [may] prove adequate and give modest gains in efficiency and comfort. Otherwise (if efficiency is the goal) Tekmar makes some amazing control systems that provided proper installation in a properly piped system and with proper adjustment (whew!) will do their best to maximize efficiency even with mis-matched emitters.0
- 120 Geothermal
- 394 Solar
