Wiring primary pump in primary secondary piping.

BrianK
Member Posts: 4
Thanks for your help. I was wondering what you use the ZC ZR connections for.
0
Comments
-
Wiring the primary pump
I just installed my first boiler with primary secondary piping and I want to know the best way to wire the primary pump to come on when any of the zones call. I installed a Buderus G124x gas fired boiler with 2 zones. I have a Taco SR504 4 zone controller and I installed a Tekmar 256 outdoor reset control. I thought I could use the third zone for the primary pump and jump out TT on each zone to TT on zone 3 but when I do that both zones call. As you can tell wiring is not my strong point. Any suggestions.
Thanks,
Brian0 -
sr504
You could use the zc zr terminals on the sr504 . Wire the primary to that.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
primary/secondary
Wiring the primary pump to ZR works great and was suggested by Joe M from Taco a while back when I asked the same question. When any of the zones call ZR is also energized.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements