Bull Headed T on Steam Main
Jeff_74
Member Posts: 46
I think I found out why there is a cap on the end of this main. In the pic, you can see that the main is headed right for a sewage pipe. Perhaps the original intaller designed access to the end of this main? The main pitches slightly toward the capped portion. Perhaps the steel strap has drooped a little.
I still wonder if it would improve the system's performance to tie into the main at its end as apposed to the bullheaded T.
I still wonder if it would improve the system's performance to tie into the main at its end as apposed to the bullheaded T.
0
Comments
-
Is this OK
Is this piping arrangement OK? On one of the mains of my one pipe system
there is a bullheaded T so the steam splits off in either direction. There are two take off's on the left and three on the right (almost toward the end of the main).
I noticed that the very end of the main has been capped and wonder if I should
have this re-piped to get rid of the bullheaded T.0 -
yes...
bull heads on steam are a non no...especially a newer boiler where the steam can have more velocity..I have seen it be ok on very old 50+ yr. old systems....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Is this T close to the boiler
If so, it should be easy to repipe, and I would. Are there any radiator connections between the T and the capped pipe?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks...
Here is a pic of the end of the main. I think it would be quite simple to plug the T and pipe to the cap. If done this way, the steam would completely reverse directions in a very short space. Is this OK.
The bioler I replaced was 65 years old so I guess this bull headed T was Ok
then.
Thanks for your help.0 -
Thanks Steamhead et al.
Yes, this piping is right next to the boiler. I took another pic to better show
the proximity of the bull headed T and the cap at the end of the main. Yes, there are two
risers between the T and the Cap. It seems the T could be capped, put an L
on the riser and strait to the cap.0 -
Wait a minute.....
before we do anything.... is there any evidence of where that capped pipe used to go?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
As you can see
Here is a pic of the piping around the boiler showing the capped main.
There's no logical place I can see where this would have tied in. And since everything is painted the same orignal green, there's no evidence of alterations
to the piping.0 -
Interesting
I think it might have gone thru the wall to the left, where that other main now goes. Maybe they added more radiation to that part of the house at some point, and decided it needed its own main?
How does the capped portion pitch- down toward the bullheaded tee, or away from it?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I never thought of that...
I'll have to check the pitch when I get home from work. The old 65 year boiler had two takeoffs...the contractor just tied in to the existing system as seen in the pics.
While I'm not an expert, I'm not sure if another main was added because this is a boxy colonial house and the main that dissappears into the wall servies 1/2 of the house. All the rads are from the same manufacturer throughout...but...
like I said, I'm not an expert. The old boiler was piped incorectly with
both main take off's BETWEEN the two risers at the boiler.0 -
That makes sense
it was probably easier to run a new main than reroute the old one, when the sewer line was installed.
You'll want to drip the end of that main into the wet return to get rid of the water that is certainly standing in the end of the pipe. And install a tee for an air vent, though I'm not sure the main is long enough (as compared to the others in the system) to need more than a small one.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
OK...
But where does the drip connection return at the boiler? I have plenty of venting at the other end of the main (Gorton #2s)...Do I want venting at both ends? Does this mean I should leave the bullheaded T on this main?
Sorry for all the questions.
Thanks very much!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements