steam header
Options
RMA
Member Posts: 55
hi all,
How critical is 24 inches from the water line of a steam boiler to the header? I have a hieght issue on a boiler replacement job. Will 18 inches be ok?
How critical is 24 inches from the water line of a steam boiler to the header? I have a hieght issue on a boiler replacement job. Will 18 inches be ok?
0
Comments
-
very critcal..
Very critical with the header distance, make me wonder if other near pipings is any importance to you...0 -
Try using
a drop header, it will give you more riser height and let you come down to meet the steam mains. Go here for some pics of drop headers:
http://www.heatinghelp.com/library.cfm#Steam Piping
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Easy buddy
RMA is asking a legit question . Anyone that's done steam has run into height issues .
Just being here and aking the question makes me think near boiler piping IS important to RMA .0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements