steam header
RMA
Member Posts: 55
hi all,
How critical is 24 inches from the water line of a steam boiler to the header? I have a hieght issue on a boiler replacement job. Will 18 inches be ok?
How critical is 24 inches from the water line of a steam boiler to the header? I have a hieght issue on a boiler replacement job. Will 18 inches be ok?
0
Comments
-
very critcal..
Very critical with the header distance, make me wonder if other near pipings is any importance to you...0 -
Try using
a drop header, it will give you more riser height and let you come down to meet the steam mains. Go here for some pics of drop headers:
http://www.heatinghelp.com/library.cfm#Steam Piping
"Steamhead"
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Easy buddy
RMA is asking a legit question . Anyone that's done steam has run into height issues .
Just being here and aking the question makes me think near boiler piping IS important to RMA .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements