Type of material for Prestige primary loop

Saggs
Member Posts: 174
i'm installing a Prestige 110 boiler and am wondering if 1" copper would be sufficient for the primary loop? Will be using a smart 40 and 3 zones of heat at a total of 50K btu's for the heat. Anyone have photos or tips? Thx alot
0
Comments
-
I used
1" Viega Fostapex to pipe a couple recently. One used a Caleffi Hydrolink as the primary loop, the other I used copper to have a solid place to hand pumps and zone valves.
At a 20 delta t 1" copper will easily move 100,000 BTU/hr
hot rod