Vaporstats and Heat Timer Model EPC
Options
Ken_40
Member Posts: 1,310
Whatsoever!
An excellent option. Since this appears not to be a true "vapor system," use the vaporstat that goes from 0 to 4 p.s.i. (L8100B-1037).
An excellent option. Since this appears not to be a true "vapor system," use the vaporstat that goes from 0 to 4 p.s.i. (L8100B-1037).
0
Comments
-
Vaporstat and Heat Timer EP
I operate a three story house with a Heatimer model EP. This is connected to a sigle pipe steam heating natural gas WM boiler (300,000 BTU). Currently both the heatimer and the boiler are controled by 2 pressuretrols. Is there any reason why I can't swap out the pressuretrols for vaporstats to gain added control over the system?0