cast iron radiators
Karl_5
Member Posts: 6
What is the formula to determine the output per section of radiator at a temp lower than 160 degrees entering water and what gpm?
0
Comments
-
EDR
1 square foot of radiation or one EDR puts out 130 BTUH @ 160* water temperture .Every 5* drop in water temperature the BTUH output drops by 10 BTUH . The question is what is the EDR of the radiator used ? I find Dan's book "EDR" very usefull with this problem. The book has just about all of the old radiator spec sheets...0 -
May I add to that?
Minor yet critical detail to Ed's excellent answer: The temperature you use to rate a radiator is the average water temperature, (AWT) not the entering supply temperature.
For example a radiator receieving 200 degree water leaving at 160 degrees has and AWT of 180. Same radiator would have the same output if you supplied 190 degree water and returned it at 170; same AWT you see.
Entering water at 170 and leaving at 150 has an AWT of 160 as in Ed's example.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements