Piping problem with Weil-McLain GoldCGt boiler
Beth_2
Member Posts: 3
Here are some pictures. Thanks for your help. B
0
Comments
-
HELP - with piping for Weil-McLain GoldCGt gas boiler
A plumber converted my oil burning system to gas and installed a Weil-McLain GoldCGt gas boiler. It has not worked right since installation 8 months ago. I have called Weil McLain directly who said the problem is in the piping, not the unit. They recommended this website as I haven't been able to resolve the problem with the installer.
Old brick rowhouse has a 2 zoned heating system (1st and 2nd floor). The thermostats work. New TACO Flochek valves have been installed on the returns and supplys of each zone (4 Flochek valves total).
Problem: The heater is not listening to the thermostat on the 2nd floor(zone 2). It is set at 55 degrees and the boiler kicks on and makes the radiators (baseboard hot water) red hot regardless of the temperature setting. The installer had me disconnect the thermostat wires for this 2nd zone (untwist the yellow and black wires)which isolated the problem but did nothing to stop the flow of hot water into those baseboards. So, I shut off the return and supply valves to the second floor. The installer hasn't returned my calls and I'm afraid he's given up leaving me with this system that doesn't work.
Before the 2nd floor heaters started to go on, there was a lot of noise - air bubbles going to the expansion tank and banging in addition to something that sounds like its spinning.
I appreciate any help you can offer and have taken photos of the system if you'd like to see it. I just don't know where to turn.
Thank you,
Beth0 -
check find a pro
first off it sounds like it's just may be a wiring issue ,if this is a 2 zone system with 2 circulators then there should be either 1 multi circulator relay board or if it's zone valves then there should be another externally mounted transformer and it should be the proper VA to drive 2 zone valves .If the original installer will not come back then he's probalby not the guy to fix it .You can use the find a pro listing onm this site and it will give you a professinal near you for you to contact ,all these pro on this site would be able to figure it out it seems like it may just be a control wiring promblem unless it is also piped completely wrong .It would help if you could post a piciture or two of what she looks like .Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
Where are you located maybe someone can help??
Ed0 -
Please post the pictures
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Pictures of Problem Weil-McLain Gold CGt Gas Boiler System
Here are the pictures. Thank you soooo much for your advice.
B0 -
you have some.....
real issues there.....is that the way the owners manual shows the piping and venting??? kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
To bad to take a good boiler and make such a mess. Supply tee between flow checks is bullheaded.
What kind of radiation do you have? Fin tube baseboard, Cast Iron Radiation, radient heat?
I don't think you should have the three way diverting valve on this system unless you have radient heat and even then it isn't piped correctly. If baseboard or CI remove the diverting valve and go primary secondary pumping.
Expansion tank?? I didn't see it. ???
You really need to find a pro and have this fixed by someone who knows what he's doing.
Ed0 -
Hello Beth
Beth, you need to get a pro in there, thats a very good boiler, but that piping is a MESS,you need to go to the left on the pipe list at the top and find a pro , just put in your zip code and call one of the ones closest to you, you will be problem free, comfortable when they are done...David
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Where?
What a mess! Where are you located?0 -
boiler mess
If you are in Ma. please call me i can help you
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
its another..
Its another Larry,Curly and Moe's job that I've seen done here in west suburbs of chicago, the company must be bigger that I thought! Just about everthing I seen the pixs needs attenion of a boiler pros.... Not a just a plumber making connection with pipings ( btw, I'm a licensed plumber)0 -
I think its a Jersey Job.
ED0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements