15 btu/sq. ft?
Constantin
Member Posts: 3,796
... if the local design conditions are right. The heat losses calculated for the home I live in are similar (Wrightsoft and HVAC-Calc) for -10°F and 91*deg;F exterior conditions. Our home also features some of the same construction techniques.
just did he load calc
for a new 3500 sq ft residence with hvac calc. 3 floors, 1st, 2nd, and finished attic. 2x6 walls w r-19, double pane low e windows. r-30 in attic. total cooling load 46,278 btu, heating 58,607. these work out to 13 btu/sq ft and 17 btu/sq. ft. do these seem accurate.0 -
Scary, huh?
I consistently get 17 BTU's/[] for new residential construction. Trust your numbers.
Alan Said it Right!
TRUST YOUR NUMBERS!
And opt for a boiler size closest to but not exceeding!
If you're really scared, recalculate your heat loss at 78F indoor temp.0 -
I'm confused. Doesn't this depend on where the house is?
My 1920's brick house in N. Illinois (design temp -10F) needs 40 BTU/sqft. So 15 BTU/sqft for new construction, presumably in a warmer climate, seems awfully high. I've always suspected that those heat loss calcs are hugely padded so you can never go wrong.0
- 87.2K THE MAIN WALL
- 118 Chimneys & Flues
- 113 Geothermal
- 164 Indoor-Air Quality
- 73 Pipe Deterioration
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 49 Job Opportunities