1 Pipes counter flo with 2 pipe
1 boiler replaces 2. 1 counter Flo.1 2 pipe dry return with ZONE VALVES Boiler over fills and from what I was told by the tech it goes up the return..I know flo check is a band aid but I will see job tomorrow and would like a heads up if possible..They did put a by pass loop on each side of zone valves,,Steam does by pass a fill the main with steam with valve closed..I ll e mail Burnham for their piping diagram as well..WHo has any info.As you can see I am no artist lol...Thanks in advance.Rich0 -
Rep
whos the Burnham rep here? Cannt remember his name..Thanks again.Rich0 -
Richard
In reviewing your drawing, the proposed drip on the system side of the counterflow zones motorized globe valve dropping down and tying into the other zones wet return is the best way to go. Depending on the size of the bypass around those valves, the steam will migrate into the others piping. If you put in the drip on the counterflow side, you shouldn't need the bypasss around the valves anymore. Just make sure you have main vents on these mains. What type of Low Water Cutoff and feeder are you using and what model of Burnham boiler is it?
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0 -
Hey Glen
Sorry I forgot your name..lol.. THANKS for the reply..I havent seen the job yet but a tech called me today about the problem.Im pretty sure its a 7 section Burnham.We mainly use Burnham, The by pass is 1/2" on both valves.. There was a problem at install and they thought it was fixed with the by-pass.. I didnt like that idea lol.So you think Im on the right track then..And awhile ago you sent me a piping diagram of a counter flo system..Still have it.. Thanks for that as well..Do you think it may be drawing a vacume??I do not want to use a check valve!if possible..Im out of Bangor Me. can I call you tomorrow or do I call the Ma. office??0 -
Richard
Your representative's name for the Maine area is Rick Gendron. You may call me if you wish at my Rhode Island Office at (401) 789-1899. I will be in and out for much of the morning but should be settled in after 2:00 pm.
Glenn Stanton
Manager of Training
Burnham Hydronics
U.S. Boiler Co., Inc.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements