Wiring Issues

jim lockard
jim lockard Member Posts: 1,059
1)Neutral and ground must be isolated to the point of service. That means to the main panel box. If you are using a subpanel you must bring the ground back seperate. So yes to main panel/ no to subpanel

2) 20 amps

3)How about a fused pullout at the appliance, gives you overcurrent protection and a disconnect all in one.
J.Lockard