steam coil ratings

clammy
clammy Member Posts: 3,162
Recently looking at a large possible commerical steam to hot water conversion for a production and warehouse building .Lots of things going on and i have done a primary heat lose but need the edr of 2 existing coils they are controller by honeywell valves it is a 2 ppe system each coils connection is 2 1/2 the feed is 3 the sytem pressure is running about 2 1/2 the coils are 2 pass copper coils measuring 74 x 32 .The building has a oversized boiler by about 2 to 2 1/2 mbtu and some buried returns very long runs about 200 back to the boiler room ,bad condensate pumps,traps takes on water and extremly high gas bills averaging about 14 grand a month and more when below 30 and the whole system was pneumatics which is gone so it's all just a rip with make up air units with all the guts removed just run rampidt .It's a hugh job and lots of variable thanks for any input peace clammy

R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,467


    Measure up coils legenth width height fins/inch #of tubes and tube size and call a coil manufacturer for a rating. You may find the original name tag if you look around Sounds like they let the place go--now they are paying for it with high fuel bills--nothing wrong with steam or pneumatic controls -but they need to be maintained