Which Steamer?
I have to bid a residential replacement steamer. There is 642 sf of radiation. The WM EG65 is good for 633 sf and the EG75 is good for 750 sf. I also have to run a small zone of baseboard off the condensate. I'd prefer to use the smaller steamer, but will it be sufficient?
Thanks in advance, Adam0 -
Thanks!
Thanks Steamhead. For future reference, what's your rule of thumb? How much "over" would you go, and why? What's the limit?0