webster vacumm system
ed wallace
Member Posts: 1,612
I am bidding on the replacement of a mills 24 boiler that originally a webster vacumm system am i going to run into a problem if i remove the vacumm trap from the system
\"Vacuum Trap\"?
Sure it's not a Return Trap or a Float Trap/Air Eliminator? According to Lost Art, the Webster Vacuum system had a vacuum pump. But Webster also marketed the Modulation system that just had a FT/AE with a vacuum check on top, and a system that also included a Return Trap.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Consulting0 -
webster
its the modulating system0 -
NO..as long as you repipe it right
vent the h!!!!! out of it and put her on a vaporstat...if you can still get one. Mad Dog
That FT/AE
probably has tappings for a sight glass. If you remove the plug in the top one you can use it for a second vent. The vacuum check should be removed also and a main vent installed- I'd use Gorton #2 vents.
As Mad Dog says, use a Vaporstat on this system.
Consulting0 -
what do you mean?
if you can still get one? a vaporstat?0