outdoor reset with indirect fired water heater
outdoor reset controls I've worked with have indirect heater function built in to them . Were you looking at a particular brand of OR control ? What brand boiler are you using ?
0
Comments
-
outdoor reset with indirect fired water heater
when installing outdoor reset with an indirect fired water heater is their a simple way to bypass the reset temperature and allow the boiler to ramp up to 180 degrees when needed for demand? i have figured out a way utilizing some relays however maybe a manufacturer has a control that eliminates reset on priority demand.
thanks for the input. jrh0 -
reset override
use a Tekmar 260. Sell a lot of them and they work...have one on my boiler. Went from a tankless operation @ 800 gal/year to an indirect with 260 and cut it to 510 gallons...worth the investment !!!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Good show Al !
Now there are some solid numbers ! Almost a gallon a day on average less fuel used.
Lets see....8/10ths a gallon a day...X 365 days =292 gallons /year. While the prices keep rising, lets just see what that is at the local rate of around 2.65/gal....HHMMMM 774$ per year...I think the payback will be relatively short...don't you? Chris0 -
what kind of tankless?
By tankless was it an on demand like a Rinnai ?
I was under the impression that an on demand system was more efficent than an indirect.0 -
Tankless
he's talking a tankless oil boiler which is a coil in the boiler requiring the boiler to be hot all the time. And i doubt a Rinnai is more eff than a modcon and an indirect for a typical familly where mom runs stuff constantly .
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Taco EXP version of switching relay controls for pumps, or zone valves have an interface terminal for an add-on outdoor reset control. If you switch the priority toggle switch to priority on position the priority zone will always over ride the outdoor reset control. For your reference I attached the instruction sheet for the PC700-2 outdoor reset control.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements