hot water rising

Donny
Donny Member Posts: 37
Try introducing heated water into tank near bottom, provide an opening 180* away and slightly lower to supply water to pump for panels to be heated, supply for heat emmiters would come off the top of the tank

Comments

  • Ericjeeper
    Ericjeeper Member Posts: 179


    Ok I am getting closer to setting up my solara array. I am concerned with the hot tank fluid rising out of the tank.. and back to the panels. What type of device do I need to stop this on both the supply and return side? Zone valves? or just a backflow preventer? But one will be facing wrong direction correct?
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,599
    Possibly...

    ... heat traps. Make them deep, say 18". Advantage is no moving parts though they may need bleeders at the high points.

    Yours, Larry
  • Ericjeeper
    Ericjeeper Member Posts: 179
    tank is just an open vessel

    My system will be closed system each side.I was just trying to figure out how to keep the heat from climbing back up the plaumbing and rising to the colder panels.
  • Ed_26
    Ed_26 Member Posts: 284
    thermosiphoning

    Read Tom Lane's book on solar. You can use check valve(s) or a zone valve which closes at the appropriate time/temperature.(or opens), which ever you choose. The simplest way to me would be to activate a zone valve with the pump control.