    noisy taco RMB-1

    has anyone had this issue with the taco mixing block
    RMB-1? I have two on one job that I looked at today and the owner said they are both very loud. I did not fire up the units to hear it my self, for the supply house is going to give us two new ones to replace them.
  • tom_49
    tom_49 Member Posts: 267


    Ricky,

    I had the same problem last year. All it was, was the internal flow checks, it was a squelling sound. Taco had me remove them, they ran great all last season. great product.

    Call taco cust. service they are very helpful. 401-942-8000

    Good luck, tom

  • maine rick
    maine rick Member Posts: 107


    did you have to put flow checks outside the units or go with out them all together.

    thanks tom
  • Leo
    Leo Member Posts: 772
    A sheet on this

    Taco has a sheet on removing the check on their web site. I used it and it worked with no ghost flow. I,m sorry I don't remember the exact spot on the site it is located.

    Leo