How much to under-fire my boiler

Steve Garson_2
Member Posts: 712
My new WM SGO-4 boiler was installed per specs and sized according to what seem to be proper measurements. In previous postings, I have been trying to trouble-shoot whistling air vents on radiators. The boiler is clean, pipes insulated. Installation of a Vaporstat with 4-oz cut-in and 8-oz cut-out has reduced the whistling a great deal, but the system still makes noises.
Steamhead suggested that the boiler might be overfired for the load. Right now, the nozzle is a 1.10 gpm nozzle that was delivered with the boiler package.
This morning was our first "design day" with a temp of 2* above zero. My house recovered from a 7* set-back with 80 minutes of burner time. After reaching 69*, the temperature was steady for the next two hours with fifteen minutes of run time.
What do I tell my oil company to install for a new nozzle? Am I saving oil by having such a fast recovery of steam?
Suggestions?
Steamhead suggested that the boiler might be overfired for the load. Right now, the nozzle is a 1.10 gpm nozzle that was delivered with the boiler package.
This morning was our first "design day" with a temp of 2* above zero. My house recovered from a 7* set-back with 80 minutes of burner time. After reaching 69*, the temperature was steady for the next two hours with fifteen minutes of run time.
What do I tell my oil company to install for a new nozzle? Am I saving oil by having such a fast recovery of steam?
Suggestions?
Steve from Denver, CO
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements