With 185* S and 165* R temps: 6.1 minute on 24 minute off with 15000 heat loss. 7 minute on 16 minute off with 22250 heatloss. 9.7 on 9.8 off @ fuul load. I assumed modulating the Baxi to 75000 b tu output with 30 gal tank. Hope this helps. 65* ambient air around tank.
0
Comments
-
someone with HDS ?
Installed a Baxi 310i w/ 2 zones. Total load is 37KBTUH. Baxi will modulate down to a minimum of 35,500. Short-cycling constantly.
Don't want to do this twice, or over do it. How many gallons of storage should I install ?
TIA,
Tony0 -
anybody ?
0 -
Tony
What kind of run times are you shooting for? Supply temps? And are the loads split evenly 50/50?0 -
info
Loads are about 60/40. Baxi runs to 185 supply. Current burner run time is about 90 seconds, once it's up to operating limit temp.
I'd like to see it run for a bit longer0 -
Thanks, Bob
What happens if the Baxi is modulated to 40,000 ? 50,000 ?
I think I can squeeze in a 20 gallon tank.
At first, before I realized how oversized I am at low fire, my return temp would fluctuate from 170 to 155 between firings. It wouldn't recover from 5F setback 30F above DTD for hours. I was using the internal circ for the system as well, with enough flow, but not enough load.
The customer, when I explained the problem, couldn't believe "that little thing is too big for my house"0 -
Tony,
50000 output, 20 gal storage: full load 19 on 6.6 off, 15000 load 7 on 16 off, 22250 load 9 on 11 off. Dropping down to 40000 doesnt seem like a good match with 20 gal storage.0 -
Tony
I input wrong values ,here are the revised numbers: full load 50000output 20 gal storage, 15 on 5.3 off, 15000 load 5.6 on 13 off, 22250 load 7 on 8 off
The Baxi's a pretty cool boiler, we just took the line on. Love the R-Max feature, makes it real versatile.0 -
Thanks again, Bob
What a great place this is, huh ?!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements