Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
steam boiler limit
doug_31
Member Posts: 1
Is it code worthy in New York to tee off a pig tail to provide operational pressure from boiler to the operational pressure switch as well as the manual reset pressure switch?
0
Comments
-
ok
Yes, unless there was a code change....But best to have two pig tails. Pig tails plug up .0 -
trap 3/4 \" vs. 1/4 \"
on some larger installations i have recently seen traps fabricated with full 3/4 " b.m. fittings in lieu of a conventional pigtail syphon trap . a little more work but sure won't jam up too quickly.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements