    1.) How much clearance around a Gorton #2 main vent should be left to combustibles?

    Specifically, I have a Gorton #2 on a riser off the end of my main which consists of a combination of various nipples and 45's to get it up under a stairwell to allow sufficient height above the main (the cellar ceiling being so low at that point)

    Under that same stairwell are also lots of electrical wires, an electrical junction box, wood framing, etc. etc.

    So, how much surround clearance (in inches) should be between the Gorton #2 and everything else?

    2.) Also, should the nipple risers for main vents be insulated like all the other piping or left exposed?

    Thanks
  • Big Ed
    Big Ed Member Posts: 1,117
    Options
    Clearance

    Combustion is not a problem with the low temperature it will reach.You would need to service the vent in the future so leave access...I would be concerned about the direction of the vents venting ,It may spit out steam.. Insulation would not hurt on a long riser....