Drop Header

gerry gill
gerry gill Member Posts: 3,078
still need to go up 24'' above the waterline minumum..the header needs slight pitch, 1/8th'' per foot is fine..thats way more than the 1'' in 20 feet of the mains...the header should at least equal the square inch area of all the take offs..the old hoffman data book says do that plus up it one size..hope this helps.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=360&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

Comments

  • thfurnitureguy_4
    thfurnitureguy_4 Member Posts: 398
    Drop Header

    I am wanting to learn more about drop headers. Is there an optimum height above the boiler to start you first elbow? Should the main horizontal header pipe be 1" larger than the boiler take offs? What kind of pitch should the header have back to the equalizer? Looking to correct poor near boiler piping on a V905 A Burnaham. The photos in the library are good but the above questions are not obvious in the photos. Thanks T.