Latest Steamer (Steamhead)
Steamhead
Member Posts: 17,387
Columbia CEG-112 in a nice little rowhouse. Didn't get a pic of the dry-fired Slant/Fin we took out (sorry, Noel). It was piped in 2-inch copper straight up to the steam mains with no header.
We reversed the direction of the header so the boiler would sit closer to the chimney, cutting down on a long smoke-pipe run.
A Gorton #2 vent on the long main and a #1 on the short main balanced the system. It's a one-pipe system using recessed cast-iron convectors.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
We reversed the direction of the header so the boiler would sit closer to the chimney, cutting down on a long smoke-pipe run.
A Gorton #2 vent on the long main and a #1 on the short main balanced the system. It's a one-pipe system using recessed cast-iron convectors.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
Steamhead
Looks mint. What size tappings does that columbia come with?
The dunkirks that I use are 2 1/2 and yours look the same but I cant tell just curious0 -
New installation
Would you mind pointing out where the Hartford loop connection is placed?0 -
Once again what a great looking job Steamhead!
Ted, The Hartford loop on this install is the cooper pipe (it looks like it may be a 2" pipe) directly to the left of the sight glass. If you look closely at the picture you can tell it is a few inches below the water line!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
More
Thanks for the "pointer", Bob!
All the steam pipes around the boiler are 2-inch, as specified. The steam tappings are both 2-inch. Larger boilers in this series call for 2-1/2-inch or 3-inch headers, but they all have 2-inch tappings.
We tied onto the existing return and ran 1-1/2-inch to form the Hartford Loop, going into the bull of the tee in the equalizer. We had to use an extra pair of elbows to shorten the horizontal pipe where it ties into the equalizer. If we hadn't done this the resulting long pipe would have caused banging.
We had some electrical trouble with this job. It looked like a bad spark module during testing, but turned out to be a wire in the old thermostat cable grounding against the steam main. The old boiler had millivolt controls so there wasn't enough voltage to make it ground out, but the Columbia's 24-volt control system made it ground out nicely. I ran a new cable and secured it away from the steam main and it worked fine.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Loop
0 -
Nice work Frank
I'm a little envious of the room you had there . Are those 2 by 1 1/2 by 1 1/2 black tees hard to come by ?0 -
Thanks, Frank & heatinghelp!
I'm the homeowner for this job, and I just wanted to publicly say thanks to Frank for being so easy to work with and doing such a great installation.
I knew nothing about heating when I went into this, and I have learned a whole lot. The best thing I did was go to heatinghelp.com and start to learn about steam! Thanks to those who keep this site running.
Regards,
Nina (in Baltimore)0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements