adding a vent

ed wallace
ed wallace Member Posts: 1,613
have a strange problem with a steam radiator it heats very slowly today I repiped from the main to the radiator all new pipes eliminated 3 1 in 90 elbows installed 1 90 elbow and 2 45 els took over 30 minutes for steam to get to radiator which is 1,000 better then no steam I am thinking of drilling and taping to add another air vent to rad is this a good idea

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    maybe. ..but

    if you disconnect the radiator from the supply valve,,how long does it take to get steam to the open pipe? also what kind of air vent did you use?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Steamhead
    Steamhead Member Posts: 17,387
    There's another problem somewhere

    How long does it take between the time the boiler produces steam and the time the steam reaches the end of the main? How long between the time steam reaches the end of the main and the ime it reaches that radiator? How long is the runout you repiped and where does it connect to the main- near the boiler, in the middle or near the end?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • John Barnes
    John Barnes Member Posts: 10


    You don't need to drill and tap a new hole. Just try a Gorton D. But first try taking the vent off completely and see how long it takes to heat up. Also, did you replace the valve into the radiator as well (or at least confirm that it is not broken, clogged or otherwise constricted)?