steamstorage tank
bob young
Member Posts: 2,177
anyone ever control a steam storage w/ internal coil[ heat exchanger ] with a solenoid valve and aqastat ? how many pounds pressure max. maintenence man scrapping spence valve and designing his own system.comments welcome
0
Comments
-
Why...
... would you want to get rid of a modulating control valve, and go with an on-off valve like a solenoid? Even if it's sized correctly (most aren't), the solendoid will "hunt" at low loads, banging on and off repeatedly. If it's seriously oversized (most are), it'll "hunt" even at high loads.
What is the steam safety valve setting? I see a lot of ASCO solenoids installed in systems that operate at 125 PSIG or under, but the safety valve that protects the system lifts at 150. I've never seen an ASCO rated for more than 125 steam.0 -
modul. valve
thanks,tony. my thoughts exactly. seems like this guy is trying to blow up this bldg.he is running ten pounds steam for a two storey facility.0 -
modul. valve
thanks,tony. my thoughts exactly. seems like this guy is trying to blow up this bldg.he is running ten pounds steam for a two storey facility.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 99 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements