EDR of Train Unit heater
Options
thfurnitureguy_2
Member Posts: 74
Any body Know the EDR of a Train 38S Unit Heater Is it 38 sq ft.?
0
Comments
-
it depends
They list three ratings, depending on the motor's RPM. At 1550 RPM the rating is 162 EDR, at 1300 RPM its 150 EDR, and at 1100 RPM its 136 EDR. The 38 refers to the approximate output at 2 psi steam, which is about 38,000 BTUH.
Hope this helps out.
Best regards, Pat0 -
EDR
Pat, Thanks for the info. That was the missing link in my EDR Total. I will check the rpm on my fan.0