EDR of Train Unit heater

Options
Any body Know the EDR of a Train 38S Unit Heater Is it 38 sq ft.?

Comments

  • Dave Meers
    Dave Meers Member Posts: 103
    Options
    it depends

    They list three ratings, depending on the motor's RPM. At 1550 RPM the rating is 162 EDR, at 1300 RPM its 150 EDR, and at 1100 RPM its 136 EDR. The 38 refers to the approximate output at 2 psi steam, which is about 38,000 BTUH.

    Hope this helps out.

    Best regards, Pat
  • thfurnitureguy_4
    thfurnitureguy_4 Member Posts: 398
    Options
    EDR

    Pat, Thanks for the info. That was the missing link in my EDR Total. I will check the rpm on my fan.