EDR of iron pipe
thfurnitureguy_4
Member Posts: 398
I need the EDR value of 3" exposed Iron pipe per foot Any ideas? Thanks
0
Comments
-
just about
1.33 sq ft EDR per linear foot. (For steam at 215 degrees)
-Michael0 -
pipe heat loss
3" iron pipe at 180* water is 221 BTU/hr
3" iron pipe at 5 PSI steam is 355 BTU/hr
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0