Return Vents
Boston help needed
Member Posts: 4
Should returns on a one pipe steam system have air vents?
0
Comments
-
As long as...
Dimension "A" is okay, and as long as the vent is AFTER the last radiator take-off, you can put them on any part of the dry return you can - preferably at least 12" before an elbow or drop: never on the run of a bull headed tee!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Follow-up...
Thanks Ken. I believe Dimension A is ok but my existing vents are within that dimension - on the drops, just above the water line (maybe 6" above the water line). Does this sound ok? Thanks so much for the help!0 -
Return Vents
Does anyone know the answer to this? Thanks for any advice!0 -
Move them up to the level of the steam main
You may need to drill and tap the main, but the vents will work much better.
Are the vents sized properly? Measure the length and diameter of each steam main and tell us what vent is on it.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Return Vents
One main is 45' long 2.5" pipe with a Gorton#2. One main is 15' long with nothing now but based on your earlier recommendation it will have a Hoffman 4A. The returns have very old radiator vents (1/8" angled) - I can't tell what brand. Thanks for all the help.0 -
Ahh, you're the same guy.....
On a one-pipe system with proper vents at the ends of the steam mains, you don't need return vents. Take them off and install 1/8" plugs in the holes.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Return Vents
One more question. This is the main that only serves the indirect radiators (in ducts) and the returns come directly from the radiators/ducts (i.e., not directly connected to the main). In that case do I need return vents and if so what type? Thanks again!0 -
Don't vent that return
if steam gets in it, it will bang. A main vent will handle the steam main and the vents on the indirects will do the rest.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thank You Steamhead
Sounds good. Thanks so much for all the advice/help. Greatly appreciated!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements