Voltage reading on a themostat

jeff_50
jeff_50 Member Posts: 13
I'm trying to set the anticipator on my thermostat.
My volt meter reads at 27, how do I interperate the
numbers on my Honeywell 87 thermostat? (It
has such values as .15, .2, .3 ,4, etc.

Thanks,

JC

Comments

  • Jim Bennett
    Jim Bennett Member Posts: 607


    The settings on the T-87 are amperage reads. You need read the amperage draw at the thermostat and then move it to the appropriate setting

    There was an error rendering this rich post.

  • Empire_2
    Empire_2 Member Posts: 2,340
    T-Stat

    You are reading 27 vac because the t-stat is not calling for heat. you are looking for amps to set the anticipator. Use calmp on amp probe wrap 18 ga. wire around the jaws and read your actual amp reading. Devide by 10.