I have a weil mclain 368st oil fire boiler the lwco seems to stick,is it wise to clean it or change it. The boiler is 11 yrs old. thank you. tom
  • tom_11
    LWCO
  • ed wallace
    ed wallace Member Posts: 1,612
    lwco sticks
    time to replace it its a safety device if it fails to turn boiler off you will have major problems please turn off your heat til its replaced
    Steamhead Member Posts: 18,207
    Consulting
  • Empire_2
    Empire_2 Member Posts: 2,340
    LWCO
    If its probe type replace it,. If its mechanical, it can be cleaned ONLY by a qualified Tech. and kept in system. This is not a safety switch that you want to second guess.
  • Michal
    Michal Member Posts: 213
    what controls do you have
    well we need to know what controls do you have what model numbers. I have seen model 67's stick cause of rust on the inside and I have seen them cut water off too low since they were not adjusted correctly.
  • tom_11
    LOWC
    I have a #67 McDonnell.Miller LWCO, i opened the bottom of the Lwco and there was some scale on the wall of the lwco, so i cleaned the wall and replaced the gasket. It works fine now. Thanks for the help. Tom
    Keep a close eye on it, Tom
    in case it sticks again. A new LWCO is much cheaper than a new boiler.
    Consulting
  • Michal
    keep eye on it
    well a friend had the same issue, he called service guy before i could get a gasket kit and he replaced it, was very pricey, but like steamhead said keep a eye on it