glen staton

pb48
pb48 Member Posts: 20
I HAD A IN5 INSTALLED LAST YEAR/ HAD A LOT OF TROUBLE WITH BANGING PIPES AND RADIATOR SPITTING WATER CALLED CONTRACTOR HE ADDED CHEMICALS TWICE WORKED A COUPLE OF WEEKS HAPPENNED AGAIN I WK FOR LOCAL UTILITY I KNOW THIS BOILER IS TO BIG FOR THE HOME I ONLY HAVE 5 RADIATORS I REMOVED 2 BURNERS PLUGED THE ORFICES BOILER RUNNING OK WITH NO CO/ IS THIS A OK FIX/ IVE BEEN OK FOR 5 WEEKS

Comments

  • Plugging Orifices

    is not an approved method of downfiring today's boilers. It will change flue gas flow through the boiler and possibly throw off the CO2 levels at the draft hood. If you need to down-fire we advise contacting our Technical Servives Dept. and they will let you know the proper size orifices to accomplish it. It is not a guessing game but rather a science. I'm also concerned about your initial problem of surging and banging. Adding chemicals to a steam boiler is not going to get rid of the real root of the cause of the surging. We advice a proper cleaning procedure such as skimming or boiling out the boiler and not to leave chemicals in the boiler unless they are needed to treat a PH problem or something similar. A real good cleaning will make a huge difference in performance and it will probably take hours and not minutes. Hope this helps.

    Glenn Stanton

    Manager of Training

    Burnham Hydronics

    www.burnham.com