Pressure Problem

Josh_10
Josh_10 Member Posts: 787
One more thing that might be a possiblity... You could have ruptured the expansion tank bladder during installation by mistakenly overpressurizing or it may be undersized. Just a thought. I see both happen all the time even by professionals.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=434&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Darryl_3
    Darryl_3 Member Posts: 6
    Pressure Problem

    I have a hot water boiler that has five zones with pumps. One zone is for an indirect hot water heater. The radiation in the house is cast iron based board and cast iron radiators. I have replaced the relief valve, fill valve and expansion tank. Every now and then I find the relief valve on the boiler leaking and the pressure at 30psi. As a test I have closed the ball valve on the fill side. Still find that the pressure climbs. Any help/suggestions is appreciated.
  • Ron Schroeder
    Ron Schroeder Member Posts: 998
    Darryl

    I would say that unless your Pressure Reducing Valve and ball valve are bypassing than you have a leaking coil in the Hot Water Maker unless you have an old tankless coil still hooked up that could be leaking.

    Bruce
  • Brad White_107
    Brad White_107 Member Posts: 10
    I agree with Bruce

    99% chance it is within the two things mentioned, more likely the in-boiler coil especially in that you have replaced the expansion tank, relief and fill valves.

    As an aside, see if there is a valve in the line to the expansion tank and make sure it is left open at all times. Also if an old gravity system with large pipes and lots of volume it may require a larger tank than you have. Just a thought.
  • A.J.
    A.J. Member Posts: 257
    pressure problem

    > I have a hot water boiler that has five zones

    > with pumps. One zone is for an indirect hot water

    > heater. The radiation in the house is cast iron

    > based board and cast iron radiators. I have

    > replaced the relief valve, fill valve and

    > expansion tank. Every now and then I find the

    > relief valve on the boiler leaking and the

    > pressure at 30psi. As a test I have closed the

    > ball valve on the fill side. Still find that the

    > pressure climbs. Any help/suggestions is

    > appreciated.



    Just one more thing, if you are on city water check your pressure to make sure that your not above 70 lbs otherwise the plumbing could be forcing your feed valve to fill.
  • A.J.
    A.J. Member Posts: 257
    pressure problem

    Just one more thing, if you are on city water check your pressure to make sure that your not above 70 lbs otherwise the plumbing could be forcing your feed valve to fill.
  • clammy
    clammy Member Posts: 3,163
    check aquastat

    I have on one or two occasions have seen the same promblem after checking that your feed water line inb completly closed run the boiler and check your aquastat setting i have seen a few which where bad and ran the bioler temp to over 200 causing the safety to pop ,also check as other have stated your indirect tanks domestic water lines isolate them and make sure they are not leaking into your boiler increasing your boilers pressure popping your safety peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Big Ed
    Big Ed Member Posts: 1,117
    Tank

    What size expansion tank is on the job?Also what make and model indirect ?