MPO - 5 section , 6 zones
Hey Ron, great looking job ! However, with that wet looking spot under the unit, is the new boiler leaking?... Weekend coming up.. Gonna goooo...
  • We replaced this beastie
    in Huntington , NY . The casting said WM Pace Boiler Co .
    I say it shoulda been called an oil hog . This is the first time I've seen a steam LWCO on a hot water boiler . To the left of the hog was a 50 gal. Bock heater that we replaced with an indirect . I liked the individual relays on the wall , 5 in all .
  • Burnham MPO
    I wish they would sell the MPO line in a knockdown version . We received the boiler from our supplier with the jacket already damaged . It's very easy to rip the sides of the jacket where the screws hold it in place . A little creative thinking and we fixed the problem .
    Me and Kenny went back for a 2nd day to wrap it up . Odd thing happened on the intial firing . Either the aquastat hung up on the first call of heat , or there was an overide . Somehow the boiler temp got to 235 degrees . This was after we reset the high limit to 180 . We ran the boiler 5 or 6 more times but couldn't duplicate what happened . Has anyone had such a temp override with the MPO before ?
    Other than those 2 little details , the job went smooth . We busted our butts ripping that monster out and setting the new one in place in less than 3 hours . Needless to say , the rest of the 1st day everyone was exhausted .
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    Nice Ron !
    And you even got to stand up all day!
    How do you like the Alliance indirects? It looks like a nice unit. Am I right in saying that Burnham "aquired" Mega-Stor? It looks very much like their units, with a white cover.
    I hope the homeowner gave you an "ataboy". You and Kenny deserve it after that one. Chris
  • Leo
    Leo Member Posts: 772
    Hey Chris
    Hey Chris,
    Megastor is Crown whiich is one of the Burnham companies.
    Leo :)
  • Leo
    Ron
    You always do NICE! work. I bet replacing that pig will save the customer money in fuel. Who said oil companies fix systems to use more oil.
    Leo
  • LarryC
    LarryC Member Posts: 330
    tight fit in electrical box?
    How big is the Electrical box that all the pump whips terminate in? Is that 9 fittings?
    LarryC
  • It's an extended box
    And yep , there's 8 wires and the conduit in the box . I've asked for bigger electrical boxes , still waiting ......
  • Chris
    The Alliance is one HEAVY indirect . Forget about handtrucking the 50 gallon or bigger down a flight of steps . I do like the levelling legs - just spin them in or out to get the tank straight . They don't have a lifetime warantee like other brands . So far after 3 years or so of installing them , they're all going good .
    The homeowner didn't give us an attaboy . All he was concerned about was shoving the boiler as close to the wall as possible and changing that water filter to the right of the boiler . He tried twisting it off while we're still working - ad while it's still live . I stopped him and told him we'd try to spin it out later . The lady of the house was real sweet though , kept asking us if we wanted drinks .
    Thanks alot Chris .
  • You heard that too ?
    I thought that old urban legend was put to rest , but every now and then you get a wiseguy who says the oil companies want to see an untuned , old piece of junk in the basement .
    This homeowner is not even one of our service or oil delivery customers . He's had another company for 50 years and still plans on keeping them . Thanks alot Leo .
  • David Sutton_6
    David Sutton_6 Member Posts: 1,079
    Hi Ronjr
    How did you like movein that puppy out??
    Just took out a 6 section HB smith last wed.
    Job looks great! did you get the normal....its so small , will it work question?.....David
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    I think that old boiler
    is older than the system it was connected to. It looks like a typical 1920s cast-iron sectional coal boiler. If those big flueways weren't baffled, laminar flow would have let lots of heat go straight up the chimney.
    M&M did make LWCO units like that for hot-water boilers. The #63 comes to mind but I'm not sure that's correct. Was some of the radiation located below the boiler? If so, that's why it was there.
    Nice work, as always.
  • Ron
    In answer to the high limit overide, I would check to be sure that the sensor for the eletronic aquastat is all of the way in the well. The wire for the sensor is encased in rather heavy heat shrink and has a tendency to be a bit on the stiff side possibly keeping it from remaining fully inserted. We have spoken to Honeywell about this and they are looking into a clip of sorts to hold it in place securely. When I had my MPO boiler installed last year I inserted a 5" nylon wire tie wrap in the well alongside the sensor to hold more secure in the well and found that to work quite well. I did notice that you did not use the 1-1/2" cast iron supply tree that as shipped with the boiler. That tree was designed with a box type pattern where the immersion well threads in that more effectively surrounds the well with heated boiler water.I'm not saying that that may have contributed to your overide but if the well happened to be touching the back of the tee you have it threaded into, it could be throwing off the sensitivity a bit. That might explain why it was OK during subsequent firings due to temperature acclimation.
    The indirect you are using is the Alliance G indirect which is a glass lined indirect that we introduced a few years back in response to difficulties with High Cloride water areas that were raising havoc with the stainless steel models. These only carry a 10 year warranty versus the limited lifetime warranty on the stainless steel models and are indeed a bit heavier.
    AS far as the MPO jacket arriving damaged is concerned, the two side panels simply are suspended or hang on the front and rear panels with 4 screws. I have been advising installers to remove the top panel (4 screws) and to lift off the two side panels before attempting to move the boiler around through the house. Exerting a bit of pressure or shoving on those side panels will cause those screws to rip out and as you stated they are easily fixed afterwards. Once again thanks for using Burnham products and for a job well done!
    Glenn Stanton
    Manager of Training
    Burnham Hydronics
    U.S. Boiler Co., Inc.
  • Weezbo
    Weezbo Member Posts: 6,231
    The new owners must Love You :)
    it looks great :) only thing i can think is did you zone and check the new indirect? i lashed one up a while back and found there was heavy ghost flow through the indirect return line ....dropped in a check and it now works acceptably.
  • Glenn
    Thanks you very much for the compliment . This is a job I'll definitely be tracking the fuel usage on . 50% is an attainable number when going from that old beast to state of the art . I'm also looking into if the homeowner was offered the outdoor reset option .
    We used our own tees and pipe instead of the header tee because it didn't feel like it threaded in right . Kenny installed the aquastat , and I double checked the insertion when we started it up . The fit was on the loose side , we did use a full 3/4 inch well , and did check the depth - the end of the well was halfway in the 1 1/2 inch tee . The problem happened only on startup after Kenny reset the control to 180 . After it happened we cycled the boiler 5 or 6 times and the problem did not reoccur . Do you think the boiler could have heated up that much past the hi limit set point ? We've seen Weil Golds overide 20 degrees after they shut down .
    With the jacket , we always take apart the MPOs before moving them about . I can't see how anyone else wouldn't do the same because it is way too easy to rip the jacket out of the screws . One thing I really don't want to be doing is fixing a brand new jacket because these boilers can't be shipped in a knockdown version .
    The special return tee - we were wondering why the return hole is 2 inch , while the special fitting chokes down the flow to 3/4 ? We also piped the relief valve in the header pipe , any forseeable problems ? I'd rather have the relief piped directly into the 1 1/2 inch port than into the return tee .
    Thanks alot Glenn for you input .
  • Haha
    You got it right . We have dozens of them left over from the hanging GEs we replace . We don't use them on those jobs because the boiler switch is literally 2 feet away from the boiler , easily reached when working on the burner . Thanks alot Dave .
  • Thanks Weezbo
    Heres what I think happened , after talking to Kenny .
    We filled the boiler and opened all the supply pipes , but opened only the return for the indirect . We turned the system on . I'm thinking the supply pipe got airbound and the aquastat didn't sense the actual boiler water temp until it started steaming . Sound wacky ? Maybe there was a huge air pocket in the boiler ?
  • Ron
    The relief valve needs to be piped into either one of the 3/4" tappings in the return manifold. We give you two to be able to cover all return pipe configurations such as straight down, from the left or from the right. The return fitting reduces the flow from the 1-1/2" connection and chokes it down through the 3/4" nozzle (nipple) to create a venturi effect within the boiler. It will speed up the discharge velocity of the water through the top nipple port where the rear section joins the first intermediate section from the rear. As that velocity is increased, there will be a veturi effect at that point creating a low pressure point which actually pulls much hotter water from the rear section in and around the nozzle to blend with the cooler return water to warm it up. From there the warmed up return water goes forward and down through all of the sections forward of the rear section where it all joins together in the bottom of the boiler at the bottom nipple port. The flow then goes through the bottom nipple port to the bottom of the rear section where it turns 90 degrees and up the rear section to the supply manifold connection. most of it goes on out to the system and some of it gets pulled back into the top of the boiler by the return water venturi effect.
    I discussed this situation you had with the override today with our engineers and they agree that the smaller inner area of a standard tee may be the cause. If you look at the inside of the supply manifold it is fairly large at the point where the aquastat well inserts into thus keeping the well a good distance in all dirctions away from possible cooler metal surfaces. This would also explain why it didn't do again after the boiler warmed up. I have been advising to use a fair quantity of teflon tape on the threads of the supply manifold and then to apply teflon paste as well over the tape (teflon on teflon). This will ensure a good snug and leakproof connection without having to overtighten the manifold. By the way....how are you and Kenny liking the built in leveling bolts? Now you don't need that box of electrical cover plates, flattened copper or steel washers anymore to level the boiler up!
    Keep up the great work and I hope to see you soon. I'll be down in Maspeth at the end of the month with some of your service people.
    Glenn Stanton
    Manager of Training
    Burnham Hydronics
  • clammy
    clammy Member Posts: 3,256
    super neat and super sweet
    As always Ron you and your crew rock excellent looking job.How sore and tried where you after yanking that hog outta there .You deservse a beer and a little a/c after that one ,again your installation are awesome and until we meet and drink a brew my head hangs low in homage to your hardwork ethics , skill and craftmanship .peace and good luck and have a great weekend clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • lchmb
    lchmb Member Posts: 2,997
    Yea
    I agree with Clammy (I think). Nice job my friend, all that room must have been great. One of these day's I'll have to get myself out there to have a beer with you and learn how in the world you guys do it.
  • Tom
    I actually know Ron's secret to success with those real tight jobs. I dropped in on one of his Friday installations last year and caught him with his secret.
    The secret involves this "magical dust" that he apparently gets from this guy in Beth Page named "Holohan". Seems he sprinkles it on the boiler and related pipe and fittings and "Whoosh" they all shrink to half size. He and Kenny then put them together, line them up and 2 hours later when the effect of the "magical dust" wears off they go right back to their original size again. Tie in the original piping, oil line, flue and wires and it's off to the next one. I did hear that Ron tried sprinkling Kenny with that stuff once to make for a bit more room on a real tight job but apparently Kenny wasn't too happy about it! The secret is out!
    Glenn Stanton
    Manager of Training
    Burnham Hydronics
  • Might have been
    condensation from filling it up with cold water . I noticed it too . Not wet , just damp .
  • I think it was
    model # 63 . Good memory Frank . Nothing at all was baffled on this boiler . Big 12 inch flue too . Thanks Steamhead .
  • OK
    We have to go back to run new oil lines , I'll change the relief valve spot to the return tee . What I meant to ask is why such a large tapping in the boiler ( 2 inch ) , if the nozzle chokes the flow down to 3/4 anyway ? Is there an application where a bigger nozzle-nipple would be used ?
    The well insertion depth was right on the money - right in the middle of a 1-1/2 inch cross tee . I think what might have happened is in my reply to Weezbo , but in that scenerio I'm not sure how the LWCO wouldn't trip . Very strange , and I'm guessing it was one of those fluke occurances . Something you see once in a lifetime . The aquastat comes from the factory preset at 200 ?
  • Clammy
    I'm still sore right now . It feels like I pulled my right arm out of the shoulder socket . Kenny got beat up pretty bad too . We had 3 other guys there for the removal , but they seem fine . When I worked in the city replacing 3 or 4 steamers a week we always used everything we had to haul the pork chops out . I guess that ethic carried over . But I'm getting too old for that kind of workout . Thanks alot Clammy .
  • Hahaha
    Now that is funny , Glenn . Holohan's magic dust . Thanks I needed a good laugh after this week .
    Lchmb , the room was kind of tight , maybe 7 by 12 and a built in work bench to the left of the heater . I really wanted to push the beast to the side and let they kids rip it out , but ... no room . I have to talk to my manager about these big ripouts . Somehow me and Kenny never learned to pace ourselves , so we go full force till the boiler is out . Thats all well and good except we're pretty much shot for a few days after . Those days of feeling indestructible are long gone .
  • Return manifold
    In order to have a closed end boss big enough and with enough meat to tap for a 3/4" nipple (nozzle) the end of the return nipple boss needs to be that size. They are all 3/4" right through the line.
    Glenn Stanton
    Manager of Training
    Burnham Hydronics
  • Just figured it out
    Obvious all along , I'm so dense . The reason the aquastat overrode the first time was that even though the boiler was full of water , there was no flow past the well - the indirect zone was full of air . I remember opening the valves to the indirect and opening the airscoop cap . What I didn't do was purge the indirect zone , or any other zone . After a few minutes of firing I felt the indirect return pipe was lukewarm . The aquastat finally picked up a temp reading from the steam . Doh !!!!!
  • Ahha!
    That will do it! Thanks for the followup Ron and stop thinking about work.....it's the weekend. Not to mention its a holiday today.....My Birthday!
    Glenn Stanton
    Manager of Training
    Burnham Hydronics
  • Ron Schroeder
    Ron Schroeder Member Posts: 995
    Happy Birthday Glenn