It has came down in the past as a water quality issue. TDS count too high.
0
Comments
-
Hydronic Heating - Vibration
We recently installed a Teledyne Laars MiniTherm II (JVS100NIDS) boiler. Its is heating the house well but it, or something, has been producing a low frequency vibration, almost a rumble.
The MiniTherm replaced a 25 year old unit that was found to have a cracked heat exchanger. We simply had the old unit removed and slid the MiniTherm in its place. The MiniTherm came with a pump (Grundfos Type UP15-42F) so we also replaced the old pump, which was working fine. The expansion tank from the old system was retained and remains in its original spot, about 6 above the boiler.
I assume that there are no moving parts inside the MiniTherm as so suspect that the vibration comes from the pump. However, when I listen closely, the vibration seems louder in the unit itself as opposed to the the pump. Perhaps thats just an acoustic amplification effect. At any rate the vibration, unfortunately, travels through the house over the hot water pipes. It's louder in some rooms than others and you can feel it coming through the floor in some rooms.
Ive thoroughly bled all of the rads, and the expansion tank was drained at the beginning of the season.
Have you any thoughts as to what could be causing this vibration?
Thanks for your help.
Gino Smecca0 -
Harmonics (?)
I have seen this once with another fin-tube boiler. Does the sound become more noticable at higher temps? Is the boiler resting on a housekeeping pad or is it secured (in some manner) to where it rests?
Need more info.
Regards,
PR
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Harmonics (?)
Hi,
Thanks for your note.
The sound seems to be fairly consistent at all temperatures. We haven't really noticed any correlation to temperature. The Boiler is resting on a concrete patio stone (24"x24"X1.5"), which in turn sits on a concrete floor. The only reason we have it elevated off the concrete floor at all is because it is in our basement and on the off chance that we have some flooding down there, we bought ourselves 1.5" of insurance. The boiler however is not secured to the concrete in any way. One other note that may be relevant, we did use some shims under the patio stone to level the boiler. A couple of pieces of scrap ducting metal to raise the front of the boiler by about 1/8" to level it off.
Thanks,
Gino0 -
Was your last
boiler cast iron?0 -
Primary/Secondary
piping is required for that boiler. The manufacturer has recommended piping configurations in the instruction booklet. Improper flow rate through the boiler can generate some strange noises. Hope this helps.
Darin0 -
Pump impellor to cutoff in volute
Check the frequency of the noise - if it's "hum' it may be a pump with the largest impellor inside a pump volute that has the cutoff so close to the impellor circumference that a small hydraulic pulse occurs when the impellor blade passes the cutoff. Example: a five bladed impellor in a pump running at 1750 rpm will generate a "hum" of around 145.8 herz. ([5 x 1750]/60).
A low frequency rumble could also be a burner flame rumble in the fire chamber of the boiler too.0 -
Last boiler
No our last boiler was copper (Raypak 134-wt).
0 -
another thing
By the way, it may be worth mentioning that the MiniTherm unit was previously installed at a friend's house. He used it for one season, and subsequently installed a forced air system. The unit then sat in his garage for 2.5 years. Don't know if this may have any bearing on the situation. My friend had no vibration at his home when the unit was operational.0 -
Did you place your hand on the concrete base and on those shims while it was making the noise, to see if that dampened it? That could indicate if the base was a problem.0 -
Does it have a gas flex
on the gas supply? These will often create the noise you are hearing.
Flow issues are critical and P/S piping is important to provide adequate flow under all conditions.
Often times a hydronic treatment quiets them down also. Rhomar Water, or Mile High Chemical make conditioners to clean that HX and keep 'em quiet.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Vibration Resolved
Thanks all for your tips and advice. I replaced the pump and the vibrations disappeared.
Gino0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements