Basement Radiator / One Pipe Steam System
I am building a room/office in our basement and would like to tap into the existing one pipe radiator system to heat the room. Im thinking of installing a radiator 12"-18 above the water line so I can control it with a thermostatic air vent. Has anyone done this with success. Im a little worried about tapping into the vertical part of the return into the boiler? All comments welcome. Thanks0 -
basement rad
At 12"-18" above the water line, you will have trouble getting the condensate back to the boiler (not enough "A" dimension. You could install a trap on the radiator and install a small condensate pump, but how about installing a small FHW loop of the boiler. It would probably cost less to do and could be run as a separate zone.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 426 Carbon Monoxide Awareness
- 116 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 109 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 991 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements