someone asked for PS photos

some nice work!

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • dann crist_2
    dann crist_2 Member Posts: 37
    PS Photos

    Someone asked for photos of some PS piping-- view this as a slide show--Bill & Vondine Kopetski home in Missoula MT.
    about 7000 sq ft rfh.
  • Bob W._3
    Bob W._3 Member Posts: 561


    And I suppose thats just their weekend place :)
  • Uni R
    Uni R Member Posts: 663
    Couple of questions...

    Very plumb and tidy and some excellent soldering!

    I'm a curious homeowner so I hope you can answer a few questions.

    Where the boiler connects to the loop, aren't those tees supposed to be less than 12" apart? Most Ultra literature says to pump into the boiler, why did you pump away from the boiler? Is that Y-strainer upside down and backwards?

    I think 15 circulators (unless I'm missing some) has to be close to a residential record. ;-)
  • dann crist_2
    dann crist_2 Member Posts: 37
    Actually

    there are a total of 12 zone pumps,one primary loop pump one secondary loop pump, one boiler pump for the heat system and one for the DHW so--17 pumps, that is not a wye strainer, it is swing check valve to prevent pump from pulling water throught the DHW tank during heat calls. The boiler doesn't know that the pump is on one side or the other of the rather small loop, anyway the boiler just needs to see plenty of flow. 12" measurement etc. doesn't seem to be an issue here as all is working beautifully.
  • hr
    hr Member Posts: 6,106
    Great piping work

    how many hours?

    Do you use different PVC for vent and intake? I see the intake has non pressure rated PVC. I think the vent side requires solid core pressure rated PVC?

    Also you may need a check on both the boiler and DHW circs to prevent short circuiting.

    Plenty of pump hp :) The Taco rep must take you to lunch often.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • thp_8
    thp_8 Member Posts: 122
    Another strange statistic

    Fabulous piping job. Clean & straight. The statistic, the energy consumption from circulators on most big jobs does not have to exceed .08 watts per square foot to meet most all heating loads. And that is with parallel pumping for back-up. In alot of cases it can be close to half of that. Looking at your pics. If you run reset and run all of these together you are in the area of 2000 watts. More than 5 and closer to 10 times what is needed to move the water. I would look into more control strategies.
  • Rich P.
    Rich P. Member Posts: 60
    Question

    Dan fabulous work, I hope the owners appreciate true art.
    Is that a purge set up on the returns? 1/2" ball valves piped to a drain cool idea- I hate frozen hoses
    Rich P
  • dann crist_2
    dann crist_2 Member Posts: 37


    Thanks for the comments
    There is a check valve on both the heat side and DHW---
    yes that is a purge assy for the entire system-only one
    hose connection required-- I agree w/ the comment concerning the wattage etc. Many of the rather small
    zones will not run much. I debated over the control strategy. I may look into buying some stock in Taco--
    Actually now that you make the suggestion-- mabe I will
    ask for a lunch or two:)
  • dann crist_2
    dann crist_2 Member Posts: 37
    Solid core pvc

    pipe was used for the exhaust side of the system