what cause sa hot water boiler to flash to steam...limit @ 190

i just came from the same exact call ---basement renovated turned into an apartment --the zone was airbound --cold water in the pipes then the pump would move a little water ---hit cold water say at 65* with a little 190* makes a lot of noise -purged the system --end of problem --

Comments

  • bluemoon
    bluemoon Member Posts: 41


    I have a hot water boiler...limit set @ 190 & satisfied...a new zone comes on line & the return hammers like crazy...steam?
  • Big Ed
    Big Ed Member Posts: 1,117
    New Zone?

    Only on the new zone? How is it hooked up to the system? Does it still make the noise if you lower aquastat to say 160*?
  • john coulson
    john coulson Member Posts: 3
    flashing

    Are you pumping away from the expansion tank? what model zone valve? is it on the supply or return?
  • steve z.
    steve z. Member Posts: 11
    Hot water / Steam

    The piping may be wrong, but a quick "patch" is to raise the fill pressure to 20 -25 psi...This will make your boiling point aroung 240 -250 degrees thus eliminating
    the flashing...Extrol precharge must be raised as well.
    There is a flow problem though....
  • terry_5
    terry_5 Member Posts: 92


    I had this problem,last year!My zone valve were place on the supply side creating the prob,Once placed on return no more prob!
  • Eric_20
    Eric_20 Member Posts: 3
    If you are using a zone valve be sure that

    you have the flow direction correct, most zone valves will water hammer when they cycle,if they are backwards.
  • bluemoon
    bluemoon Member Posts: 41


    >>>We've located a 2nd circulator in a remote closet in the basement w/2 zone valves serving 2 radiant floors...this zone maybe pulling from the boiler return...then when another zone comes on & feeds cold water into the return...a little thunder storm develops?...system was last renovated 12 years ago...been fine all along...???