what cause sa hot water boiler to flash to steam...limit @ 190
oil-2-4-6-gas
Member Posts: 641
i just came from the same exact call ---basement renovated turned into an apartment --the zone was airbound --cold water in the pipes then the pump would move a little water ---hit cold water say at 65* with a little 190* makes a lot of noise -purged the system --end of problem --
I have a hot water boiler...limit set @ 190 & satisfied...a new zone comes on line & the return hammers like crazy...steam?0 -
New Zone?
Only on the new zone? How is it hooked up to the system? Does it still make the noise if you lower aquastat to say 160*?0 -
flashing
Are you pumping away from the expansion tank? what model zone valve? is it on the supply or return?0 -
Hot water / Steam
The piping may be wrong, but a quick "patch" is to raise the fill pressure to 20 -25 psi...This will make your boiling point aroung 240 -250 degrees thus eliminating
the flashing...Extrol precharge must be raised as well.
There is a flow problem though....0 -
I had this problem,last year!My zone valve were place on the supply side creating the prob,Once placed on return no more prob!0 -
If you are using a zone valve be sure that
you have the flow direction correct, most zone valves will water hammer when they cycle,if they are backwards.0 -
>>>We've located a 2nd circulator in a remote closet in the basement w/2 zone valves serving 2 radiant floors...this zone maybe pulling from the boiler return...then when another zone comes on & feeds cold water into the return...a little thunder storm develops?...system was last renovated 12 years ago...been fine all along...???0