power
Dale
Member Posts: 1,317
Just remember you have 24 volts and 24 times amps = 40 va so the typical amp load you don't want to exceed is about 1.7 amps at 24 volts output. If you load more than that you drop the output voltage to less than 24. If you exceed it too much the things designed to open at 24 volts won't open or will chatter.
0
Comments
-
power conversion
does anyone remember how tho convert voltamps to watts for loads on a transformer0 -
Isn't it the typical 240 watts, 120 volts = 2 amps...or 2 amps, 120 volts = 240 watts? Multiply or divide, depending which way you are headed?Just a guy running some pipes.0 -
Volt-Amps are the same as Watts plus or minus the power factor.0 -
Watts...
Power or (watts) = Volts X Amperes/ (P=ExI)0 -
Correct
Power factor is only considered if you have a load like a motor of some kind. I think he wants to see the total watts on a lo voltage circuit. After the step down in voltage, he wants the power consumption.. I think...:)0 -
VA to watts conversion
To relate VA to watts, you first must know what type of load you're connecting to. Volt-Amps is apparent power. Watts is real power. Only for a purely resistive load does VA = watts.0 -
Uglys
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements