Residential 30psi Boiler Relief Valve drips in summmer, Why?

jrh_2
jrh_2 Member Posts: 1
Residential 30 psi. Hot Water Boiler Relief Valve drips in summer. Drips about .25 gal in 24 hours. Why? I have replaced relief valve twice in two days. Continues to drip. What could I do or check to stop this problem.

Comments

  • John@Reliable_10
    John@Reliable_10 Member Posts: 99
    Why?

    Water psi set to high. But most likely reason is a waterlogged compression tank or a under pressurized x-tank. Last in could be a bad (leaking) tankless coil if one is on system. If this doesn’t make sense to you please call a pro
  • Jerry_15
    Jerry_15 Member Posts: 379


    Can't improve on that call. Straight to the point.
  • Dale
    Dale Member Posts: 1,317
    pressure

    I would add to the other suggestions a bad manual fill valve, very common for an old valve to leak through a bit. If you enjoy plumbing I would change the old valve.
  • CHARLES_4
    CHARLES_4 Member Posts: 61
    Relief valve

    And to think no one thought to ask what the static pressure was in the boiler...
  • Dave Stroman
    Dave Stroman Member Posts: 766


    Sometimes relief valves just leak. If there is nothing causing too high of pressure, just replace it.

    Dave in Denver

    There was an error rendering this rich post.

  • Weezbo
    Weezbo Member Posts: 6,232
    it is doing that because,...

    it wants attention. *~/:) thats the truth .
  • terry_5
    terry_5 Member Posts: 92


    Drain expansion tank completely,
  • Jerry_15
    Jerry_15 Member Posts: 379


    I've never had much luck re-charging ex tanks. I usually just replace them. Same with blow offs. Once they go they often won't reseat even if the pressure is right. A test gauge on a hose bibb in the system saves a lot of conjecture. Good luck